CHAPTER 6: ACTUAL VALUES 6.3 METERING
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 6-39
6.3.1.3 Power
Actual> Metering > Primary Values > Power
NOTE: If voltage inputs are configured in Delta connection and the auxiliary voltage input is set as Vx, measurements of
single phase power value cannot be duly calculated, and therefore, its value is zero. For the three-phase power value, the
system uses the ARON method, or two-wattmeters method.
NOTE 2: W
hen currents and neither voltages are not available in the F650, default value for power factor wil be indicated
as zero.
V2 Primary KV
Vab Primary KV
Vbc Primary KV
Vca Primary KV
Va Primary KV
Vb Primary KV
Vc Primary KV
Vn Primary KV
Vx Primary KV
VBB Primary KV
VL Primary KV
DESCRIPTION UNITS
Phase A Real Pwr MW
Phase A Reactive Pwr MVAr
Phase A Apparent Pwr MVA
Phase B Real Pwr MW
Phase B Reactive Pwr MVAr
Phase B Apparent Pwr MVA
Phase C Real Pwr MW
Phase C Reactive Pwr MVAr
Phase C Apparent Pwr MVA
3 Phase Real Pwr MW
3 Phase Reactive Pwr MVAr
3 Phase Apparent Pwr MVA
Phase A Power Factor N/A
Phase B Power Factor N/A
Phase C Power Factor N/A
3 Phase Power Factor N/A