5-16 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
5.2 PRODUCT SETUP CHAPTER 5: SETPOINTS
given IP destination is found.
Note that this setting is only valid on port B if port REDUNDANCY is set to INDEPENDENT.
Static RTX IP: This setting sets the destination IPv4 route.
Static RTX MASK: This setting sets the IP mask associated with the
route.
Static RTX GWY: This setting sets the gatew
ay to reach the destination IP route.
Important Notes:
1. Host routes are not supported at present.
2. The route mask has IPv4 mask format. In binary this should be a set of contig
uous bits of 1 from left to right, followed
by one or more contiguous bits of 0.
3. The route destination and mask must match.
This can be verified by checking that RtDestination & RtMask == RtDestination
Example of good configuration: RtDestination= 10.1.1.0
; Rt Mask= 255.255.255.0
Example of bad configuration: RtDestination =
10.1.1.1; Rt Mask= 255.255.255.0
4) The route destination must not be a connected network.
5) The route gateway must be on a connected network. This rule applies to the gateway address of the default route as
well.
5.2.2 MODBUS user map settings
The ModBus user map definition. 256 records, selectable from the complete relay ModBus map, from the ModBus user
map. For more detailed information go to appendix B in this manual.
Product Setup > ModBus User Map
Name Default Value Step Range
Address 00 0000 [0000 : FFFF]
Address 01 0000 [0000 : FFFF]
... ...
Address 254 0000 [0000 : FFFF]
Address 255 0000 [0000 : FFFF]