6-26 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
6.2 STATUS CHAPTER 6: ACTUAL VALUES
See the following figure:
Figure 6-1: Switchgear contacts
6.2.9 Calibration status
This screen can be accessed at Actual> Status > Calibration, and it includes the internal calibration status for the relay.
Table 6-28: Calibration status
FACTORY CALIBRATION: This value is active when the relay calibration settings are the default values (no calibration).
CALIBRATION ERROR: Error shown when there is a problem in the calibration settings (wrong values).
CALIBRATION DATE: This value is showing date when relay was calibrated.
CALIBRATION
FACTORY CALIBRATION
CALIBRATION ERROR
CALIBRATION DATE
SWGR X FAIL TO OPEN
SWGR X FAIL TO CLOSE
SWITCH X OPEN
INIT
SWITCH X CLOSE
INIT
SWITCH X B
INPUT
SWITCH X A STATUS
SWITCH X A
INPUT
SWITCH X B STATUS
SWITCH X OPEN
SWITCH X
CLOSED
SWITCH X
00
_
ERROR
SWITCH X
11
_
ERROR
Switchgear logic
module