10-4 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
10.4 ISOLATION TESTS CHAPTER 10: COMMISSIONING
10.4 Isolation tests
During all tests, the screw located on the rear of the relay must be grounded.
For verifying isolation, independent groups are created, and voltage is applied as follows:
2200 RMS volts will be applied progressively among all terminals in a group, short-circuited between them and the
case, during one second.
2200 RMS volts will be applied progressively between groups, during one second.
WARNING: No communication circuit shall be tested for isolation.
Groups to be created depend on the type of modules included in F650, selectable according to the model.
The following table shows the different groups depending on the module type:
SOURCE 1:
G1: H
10, H18
G2: H13, H14, H15
SOURCE 2:
G1: H1, H9
G2: H4, H5, H6
MAGNETIC MODULE.
G1: A5..
A12
G2: B1..B12
I/O F1 (MIXED)
G1 (Inp
. 1): F1..9
G2 (Inp
. 2): F10..18
G3 (Out
.): F19..36
I/O F2 (SUPERVISION)
G1 (Sp
v 1): F1..4
G2 (Inp
. 1): F5..9
G3 (Inp
. 2): F10..14
G4 (Sp
v 2): F15..18
G5 (Out
.): F19..30
G6 (Out
.): F31.36
I/O G1 (MIXED)
G1 (Inp
. 1): G1..9
G2 (Inp
. 2): G10..18
G3 (Out
.): G19..36
I/O G4 (32DI)
G1 (Inp
. 1): G1..9
G2 (Inp
. 2): G10..18
G3 (Inp
. 3): G19..28
G4 (Inp. 3): G29..36
I/O G5 (analog)
G1 (Inp. 1): G1..9
G2 (Inp. 2): G10..18

Table of Contents