CHAPTER 5: SETPOINTS 5.4 PROTECTION ELEMENTS
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-59
5.4.3.2 Phase instantaneous overcurrent element- phase high/low (50PH/ 50PL)
The Phase instantaneous overcurrent element has a setting range from 0.05 A to 160 A. It can be set as instantaneous or
timed, with the timer selectable between 0.00 and 900 seconds. The input quantities may be chosen as Fundamental
phasor magnitude or RMS magnitude as required by the application. The element incorporates a reset time selectable
between 0 and 900 seconds.
This element also incorporates a block input for disabling the pickup and trip signals. The logic outputs for the element are
the pickup and trip flags, independent for each phase, and general pickup and trip flags.
The snapshot event setting enables or disables the snapshot event generation for these elements.
SETPOINT> PROTECTION ELEMENTS> SETPOINT GROUP X> Phase Current >
> Phase IOC High > Phase IOC High 1> Phase IOC High 2 > Phase IOC High 3
> Phase IOC Low > Phase IOC Low 1 > Phase IOC Low 2 > Phase IOC Low 3
setting Description Name Default Value Step Range
Function permission Function DISABLED N/A [DISABLED – ENABLED]
Input type Input PHASOR(DFT) N/A [PHASOR – RMS]
Pickup level Pickup Level 30.00 0.01 A [0.05 : 160.00]
Trip time Trip Delay 0.00 0.01 s [0.00 : 900.00]
Reset time Reset Delay 0.00 0.01 s [0.00 : 900.00]
Snapshot event generation Snapshot Events ENABLED N/A [DISABLED – ENABLED]