11-2 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
11.1 EXAMPLE 1: COMMUNICATION & PROTECTION SETTINGS CHAPTER 11: APPLICATION EXAMPLES
Click ON key.
Ethernet LAN (10/100 Base T rear port of the relay)
In the Laptop choose My PC-Control Panel-Network-Protocols-Protocol TCP/IP-Advance and set in IP Address screen
the following:
IP Address 192.168.37.126
Netmask 255.255.255.0
In the front of F650 go to the Main Settings screen.
choose Change Settings .
Choose Comm Settings and press down the rotating knob or down key.
Choose Network 0 . It is displayed IP Address OCT 1 and set it according to the following table:
Go to General Settings . General Settings 0 is now displayed.
Set ModBus Port Number to 502 .
Set ModBus Address COM1 to 254 .
Move clockwise the rotating knob or press the down key to find Press Enter to End and press it down to validate the
setting.
Connect a crossover 10/100 MB Ethernet cable from PC to the relay.
Open the EnerVista 650 SETUP program in the PC and under Communication Computer menu and set:
IP Address 192.168.37.125
Port 502
Unit Identifier 254
Control Type to ModBus/TCP
Startup Mode to Communicate with relay
Click ON key.
The program starts connection with the relay showing the progress screen.
Sequence
Action Setting Action
---- IP Address OCT 1 Set to 192
Move rotating knob clockwise IP Address OCT 2 Set to 168
Move rotating knob clockwise IP Address OCT 3 Set to 37
Move rotating knob clockwise IP Address OCT 4 Set to 125
Move rotating knob clockwise Netmask OCT 2 Set to 255
Move rotating knob clockwise Netmask OCT 3 Set to 255
Move rotating knob clockwise Netmask OCT 4 Set to 0
Move rotating knob clockwise Netway IP OCT 1 Leave default setting without any change
Move rotating knob clockwise Netway IP OCT 2 Leave default setting without any change
Move rotating knob clockwise Netway IP OCT 3 Leave default setting without any change
Move rotating knob clockwise Netway IP OCT 4 Leave default setting without any change
Move rotating knob clockwise Press INTRO Press enter to validate settings