CHAPTER 6: ACTUAL VALUES 6.2 STATUS
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 6-11
The AUTORECLOSE INPUTS are signal configurable by the user at Setpoint > Relay Configuration > Protection Elements
to:
AR LEVEL BLOCK: programmable signal to block the autoreclose unit by level
AR PULSE BLOCK: programmable signal to block the autoreclose unit by pulse
AR PULSE UNBLOCK: programmable signal to unblock the autoreclose unit by pulse
AR INITIATE: programmable signal to initiate the autoreclose.
AR CONDS INPUT: programmable signal to set the conditions to be met before executing a breaker close.
AR PULSE BLOCK
AR PULSE UNBLOCK
AR INITIATE
AR CONDS INPUT
AUTORECLOSE INTERNAL STATUS
AR CLOSE BREAKER
AR OUT OF SERVICE
AR READY
AR LOCKOUT
AR BLOCK
AR RCL IN PROGRESS
AR LCK BY ANOMALY
AR LCK BY FAIL OPEN
AR LCK BY FAIL CLOSE
AR LCK BY USER
AR LCK BY CONDS
AR LCK BY TRIPS
AR LCK BY SHOTS
AR BLK AFTER 1 SHOT
AR BLK AFTER 2 SHOT
AR BLK AFTER 3 SHOT
AR BLK AFTER 4 SHOT
AR BLOCK BY LEVEL
AR BLOCK BY PULSE
AR STATUS
AR LOCKOUT MODE
AR BLOCK MODE
AUTORECST_61850