7-48 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
2.2.4.3 neuPTOV
This logical node class is used for neutral overvoltage and has 6 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
2.2.5 PTUV (Undervoltage)
2.2.5.1 phsPTUV
This logical node class is used for phase undervoltage and has 3 instances inside the device.
Settings
StrVal ASG Start Value O Pickup Level (3 – 300)
OpDlTmms ING Operate Delay Time O Trip Delay ( 0 – 900000 )
Units in miliseconds
RsDlTmms ING Reset Delay Time O Reset Delay ( 0 – 900000 )
Units in miliseconds
PTOVEna SPG Function TOV enable E Function
PTOV class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
PTOV Overvoltage
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Str ACD Start M TOV PKP
Op ACT Operate O
TOV OP
Blk ACT Block E TOV BLK
Settings
StrVal ASG Start Value O Pickup Level (3 – 300)
OpDlTmms ING Operate Delay Time O Trip Delay ( 0 – 900000 )
Units in miliseconds
RsDlTmms ING Reset Delay Time O Reset Delay ( 0 – 900000 )
Units in miliseconds
PTOVEna SPG Function TOV enable E Function
PTUV class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
PTUV Undervoltage
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Str ACD Start M TUV PKP