7-198 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
What are the conditions for the time (T) attribute in the SelectWithValue
and/or Operate request
Deprecated
Is pulse configuration supported (compare pulseConfig) Deprecated
What is the behaviour of the DUT when the check conditions are set
Is this behaviour fixed, configurable, online changeable
N synchrocheck
N interlock-check
DUT ignores the check value and always
perform the check
Which additional cause diagnosis are supported
Y Unknown
Y Not-supported
Y Blocked-by-switching-hierarchy
N Select-failed
Y Invalid-position
Y Position-reached
N Step-limit
Y Blocked-by-Mode
N Blocked-by-process
N Blocked-by-interlocking
N Blocked-by-synchrocheck
Y Command-already-in-execution
N Blocked-by-health
N 1-of-n-control
N Abortion-by-cancel
Y Time-limit-over
N Abortion-by-trip
Y Object-not-selected
Edition 1 specif values:
N Parameter-change-in-
execution
Edition 2 specific values:
Y Object-already-selected
N No-access-authority
N Ended-with-overshoot
N Abortion-due-to-deviation
N Abortion-by-communication-loss
N Blocked-by-command
N None
Y Inconsistent-parameters
Y Locked-by-other-client
N Parameter-change-in-
execution
How to force a “test-not-ok” respond with SelectWithValue request Device in local mode
How to force a “test-not-ok” respond with Select request
How to force a “test-not-ok” respond with Operate request DOns: Sending T=1
SBOns: Sending T=1
DOes: Sending T=1
SBOes: Sending T=1