7-206 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
10 PIXIT for Control model
Gs9 1, 2 Are subscribed GOOSE with test=T (Ed1) / simulation=T (Ed2)
accepted in test/simulation mode
N
Gs10 2 What is the behaviour when a subscribed GOOSE message with
TAL = 0 is received by the subscriber.
The message is ignored. The mechanism
applies where the new GOOSE message is not
received within a TAL.
Gs11 2 What is the behaviour when a subscribed GOOSE message hasn’t
the expected data structure.
The message is ignored. The mechanism
applies where the new GOOSE message is not
received within a TAL.
ID Ed Description Value / Clarification
Ct1 - What control models are supported
(compare PICS)
Deprecated
Ct2 1, 2 Is the control model fixed, configurable and/or dynamic
Configurable & Dynamic
Ct3 - Is TimeActivatedOperate supported (compare PICS or SCL) Deprecated
Ct4 - Is “operate-many” supported (compare sboClass)
Deprecated
Ct5 1
Will the DUT activate the control output when the test attribute is set
in the SelectWithValue and/or Operate request (when N test
procedure Ctl2 is applicable)
N
Ct6 - What are the conditions for the time (T) attribute in the SelectWithValue
and/or Operate request
Deprecated
Ct7 - Is pulse configuration supported (compare pulseConfig) Deprecated
Ct8 1, 2 What is the behaviour of the DUT when the check conditions are set
Is this behaviour fixed, configurable, online changeable
N synchrocheck
N interlock-check
DUT ignores the check value and always
perform the check