7-208 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
11 PIXIT for Time synchronisation model
Ct15 1, 2 Does the IED accept a SelectWithValue / Operate with the same control
value as the current status value
Is this behaviour configurable
DOns: N
SBOns: N
DOes: N
SBOes: N
Configurable N
Ct16 1, 2 Does the IED accept a select/operate on the same control object from 2
different clients at the same time
DOns: N
SBOns: N
DOes: N
SBOes: N
Ct17 1 Does the IED accept a Select/SelectWithValue from the same client
when the control object is already selected (Tissue #334)
SBOns: N
SBOes: N
Ct18 1, 2 Is for SBOes the internal validation performed during the
SelectWithValue and/or Operate step
SelectWithValue and Operate
Ct19 - Can a control operation be blocked by Mod=Off or [On-]Blocked
(Compare PIXIT-Sr5)
Deprecated
Ct20 1, 2 Does the IED support local / remote operation Y (Only for XCBR)
Ct21 1, 2 Does the IED send an InformationReport with LastApplError as part of
the Operate response- for control with normal security
SBOns: N
DOns: N
Ct22 2 How to force a “parameter-change-in-execution” SBOns:Not Applicable
SBOes:Not Applicable
Ct23 1, 2 How many SBOns/SBOes control objects be selected at the same time? SBOns: n = "1"
DOns: n = "1"
Ct24 1, 2 Does the DUT support any operate timeout >0 Y
Ct25 1, 2 When CDC=DPC is supported, is it possible to have DPC (Controllable
Double Point) go to the intermediate state? (00)
N
ID Ed Description Value / Clarification
Tm1 1, 2 What time quality bits are supported (may be set by the IED) Y LeapSecondsKnown
N ClockFailure
Y ClockNotSynchronized.
Tm2 1, 2 Describe the behaviour when the time server(s) ceases to
respond
What is the time server lost detection time
On one time server: An event is generated
On all time servers: An event is generated
180 seconds
Tm3 1, 2 How long does it take to take over the new time from time server 2 seconds
Tm4 1, 2 When is the time quality bit “ClockFailure” set Never
Tm5 1, 2 When is the time quality bit “Clock not Synchronized” set 60 seconds after the time server(s) ceases to
respond.
Tm6 - Is the timestamp of a binary event adjusted to the configured
scan cycle
Deprecated
Tm7 1 Does the device support time zone and daylight saving Y
Tm8 1, 2 Which attributes of the SNTP response packet are validated Y Leap indicator not equal to 3
Y Mode is equal to SERVER
N OriginateTimestamp is equal to value
sent by the SNTP client as Transmit
Timestamp
Y RX/TX timestamp fields are checked for
reasonableness
Y SNTP version 3 and/or 4
N other (describe)