APPENDIX I: FACTORY DEFAULT CONFIGURATION I.1 FACTORY DEFAULT SETTINGS
GEK-106310-AF F650 DIGITAL BAY CONTROLLER i-23
Multiplier factor for the pulse counter CntPulses Factor X 1.000
0.00
1
[0.000 : 65000.000]
Overflow value for the pulse counter CntPulses Overflow X 65535 1 [0 : 1000000]
Board selection for the pulse counter
CntPulses Board
Origin X
F N/A [F,G,H,I]
Input index inside the selected board
CntPulses Input Origin
X
1 1 [1 : 32]
Note: X is the pulse counter index, up to 8.
SETPOINT > CONTROL ELEMENTS > ANALOG COMPARATORS
SETTING DESCRIPTION NAME DEFAULT VALUE STEP RANGE
USER
VALUE
Generic Analog Function Permission Analog Function DISABLED N/A [DISABLED – ENABLED]
Generic Snapshot Events Generation
Analog Snapshot
Ev
ents
DISABLED N/A [DISABLED – ENABLED]
Analog Input Value Selection Analog Input X None N/A [All available analog values]
Analog Maximum Threshold Value Analog Maximum X 1.000
0.00
1
[-100000.000 : 100000.000]
Analog Minimum Threshold Value Analog Minimum X 1.000
0.00
1
[-100000.000 : 100000.000]
Analog Delay for Activation Signal Analog Delay X 0.00
0.01
s
[0.00 : 900.00]
Analog Hysteresis for the Deadband Analog Hysteresis X 1.0 0.1 [0.0 : 50.0]
Analog Direction for Activation Inside or
Ou
tside the Deadband
Analog Direction X OUT N/A [IN-OUT]
Note: X is the analog comparator index, up to 20
SETPOINT > CONTROL ELEMENTS > FREQUENCY RATE OF CHANGE
FREQUENCY RATE OF CHANGE 1 > FREQUENCY RATE OF CHANGE 2 > FREQUENCY RATE OF CHANGE 3
SETTING DESCRIPTION NAME DEFAULT VALUE STEP RANGE
USER
VALUE
Function Permission Function DISABLED N/A [DISABLED – ENABLED]
Direction of the frequency change Freq. Rate Trend INCREASING N/A
[INCREASING -
DECRE
ASING - BI-
DIRECTIONAL]
Operation Value in Hz/s Freq. Rate Pickup 0.50
0.01
Hz
/s
[0.10 : 10.00]
Minimum required voltage in % nominal
vo
ltage
Freq. Rate OV Supv 40.00
0.01
%
[0.00 : 110.00]
Minimum Frequency Threshold Freq. Rate Min 45.00
0.01
Hz
[20.00 : 80.00]
Maximum Frequency Threshold Freq. Rate Max 65.00
0.01
Hz
[20.00 : 80.00]
Frequency rate Trip Delay Freq. Rate Delay 0.00
0.01
s
[0.00 : 60.00]
Snapshot Events Generation Snapshot Events ENABLED N/A [DISABLED – ENABLED]
SETPOINT > CONTROL ELEMENTS > LOAD ENCROACHMENT
LOAD ENCROACHMENT 1 > LOAD ENCROACHMENT 2 > LOAD ENCROACHMENT 3
SETTING DESCRIPTION NAME DEFAULT VALUE STEP RANGE
USER
VALUE
Function Permission Function DISABLED N/A [DISABLED – ENABLED]
Minimum positive-sequence voltage
re
quired
Min. Voltage 25.00
0.01
V
[0.00 : 300.00]
Impedance reach of the element Reach 1.00
0.01
Ohm
[0.02 : 250.00]

Table of Contents