I-38 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
I.2 FACTORY DEFAULT CONFIGURATION APPENDIX I: FACTORY DEFAULT CONFIGURATION
..... ......
INTERLOCK(LOGIC) Not configured
FINAL STATES AND(LOGIC) Not configured
FRONT KEY Not configured
INPUT Not configured
VIRTUAL OUTPUT Not configured
TIMEOUT Not configured
CHANNELS Not configured
Operation24 Not configured
INTERLOCK(LOGIC) Not configured
FINAL STATES AND(LOGIC) Not configured
FRONT KEY Not configured
INPUT Not configured
VIRTUAL OUTPUT Not configured
TIMEOUT Not configured
CHANNELS Not configured
SETPOINT > RELAY CONFIGURATION > EVENTS
event NAME SOURCE SIGNAL LOGIC SOURCE LOGIC
EV1 Not Configured
EV2 Not Configured
... ...
EV128 Not Configured
SETPOINT > RELAY CONFIGURATION > SWITCHGEAR
SWITCHGEAR SETTING VALUE/SOURCE SIGNAL LOGIC SOURCE LOGIC
SWITCHGEAR 1
CONTACTS 52b
OPENING TIME 1000
CLOSING TIME 1000
CONTACT A SOURCE N/A
CONTACT B SOURCE CONT IP_F_CC1 (52b)(CC1)
OPEN TEXT 52 OPEN
ALARM NO
CLOSED TEXT 52 CLOSE
ALARM NO
ERROR 00 TEXT 52 ERROR
ALARM N/A
ERROR 11 TEXT 52 UNDEFINED
ALARM N/A
OPENING INIT OPERATION BIT 2
CLOSING INIT OPERATION BIT 1
SETPOINT > RELAY CONFIGURATION > OPERATIONS
OPERATION OPERATION TEXT SETTINGS VALUE/SOURCE