CHAPTER 5: SETPOINTS 5.3 SYSTEM SETUP
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-33
• Underfrequency (81U)
•Overfrequency (81O)
• Frequency Rate of Change (81df/dt)
o Misc:
• Broken Conductor (I1I2)
•Load Encroachment
• Rotor Blocked (48)
• Setting Groups
•Recloser (79)
• Oscillography
• Synchrocheck (25)
•Fault Locator
• Max. number of starts (66)
• Fuse Failure (VTFF)
• Data Logger
• Comparator
•Switchgear
•Breaker
When the Out of Service status goes to ON, or the setting has been changed to Enabled, the ready LED changes to red. Be
careful if the ready LED is linked to an output, because the output will not change its state. To set an output to the ready
state, see the factory default Logic & Configuration. Take notice that VO_000 is set to the output instead of VO_099
The following figure shows the flow chart of these states
Only if there is a change
from Disabled to Enable
Only if there is any change from Enabled to
Disabled
Only if there is any
change from Disabled to
Enabled
Only if LOGIC:
Relay Out Of Service
goes from Enabled to
Disabled
SETTING:
Relay Out
Of Service
RELAY IN
SERVICE
LOGIC:
Relay Out
Of Service
RELAY OUT
OF SERVICE
START
Ready
LED OFF
Ready
LED ON
OoS status
ON
OoS status
OFF
OUT OF SERVICE
FLOWCHART