CHAPTER 5: SETPOINTS 5.10 LOGIC CONFIGURATION (PLC EDITOR)
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 5-177
**NOTE1: For firmware version 7.20 or above, two new inputs have been added; PLC_BOOL_ON and PLC_BOOL_OFF. These
two inputs are set always to PLC_BOOL_ON =1 and PLC_BOOL_OFF =0 and their values are not accessible via protocol and
cannot be modified.
Example of logic signals in F650 logic configuration:
Table 5-98: Logic signals in F650
MULTIPLIER of two digital or analog inputs
DIVIDER of two digital or analog inputs
ADDER of two digital or analog inputs
SUBTRACTOR of two digital or analog inputs
LOGIC SIGNALS EXAMPLES
SIGNAL DESCRIPTION TIME DIAGRAM
SET When the input
signal is set t
o 1 the
output signal
remain fixed to 1
until a reset signal
is received.
RESET When the input
signal is r
eset to 1
the output signal
remain fixed to 0.
ONS The input signal is
p
ulsed. The width of
the output pulse is
the same as that of
the PLC cycle
TIMER With selectable
time
(MASK), one
SET input and one
RESET input
1
0
1
0
1
0
1
ut
0
1
0
1
ut
0
1
SET input
0
1
RESET input
0
1
Output
0
T
(
ms
)
T1 T2 T1+T2=T