7-196 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
8 PIXIT for GOOSE publish model
Description Value / Clarification
Can the test (Ed1) / simulation (Ed2) flag in the published GOOSE be
set
N
What is the behaviour when the GOOSE publish configuration is
incorrect
DUT keeps GoEna=F.
Configuration tool does not allow wrong
configuration to be uploaded into device. E.g.:
empty dataset.
Published FCD supported common data classes are SPS, INS, ENS, ACT, ACD, MV, CMV, SAV, WYE,
DEL, SEQ, INC, ENC, SPC, DPC, INC, ENC. (Only
the elements with FC=ST or MX are published).
What is the slow retransmission time
Is it fixed or configurable
Configured by SCL or GoCB MaxTime
What is the fastest retransmission time
Is it fixed or configurable
Fixed. MinTime = 5 ms
Can the GOOSE publish be turned on / off by using
SetGoCBValues(GoEna)
Y
What is the initial GOOSE sqNum after restart sqNum = 1
May the GOOSE data set contain:
- structured data objects (FCD)
- timestamp data attributes
Y
Y (timestamp attributes are not supported)
How is the retransmission curve after a change.
sqNum = 0 New change
sqNum = 1 -> 5ms later with TAL = 1000
sqNum = 2 -> 10ms later with TAL = 1000
sqNum = 3 -> 15ms later with TAL = 4000
sqNum = 4 -> 1000ms later with TAL = Update
time* multipled by 4
sqNum = 5 -> Update time* later with TAL =
Update time* multipled by 4
sqNum = 6-> Update time* later with TAL =
Update time* multipled by 4
sqNum = 7 ……..
………...
………….
*Update time is configured in the ICT

Table of Contents