The minimum and maximum main values are:
-For Current:0 to 160 A (secondary values)
-For Voltage:0 to 300 V (secondary values)
-For frequency:20 to 70 Hz
-For Angles: 0 to 360 (only in firmware version 5.00 and higer, the deadband used for angles is the dbAng parameter)
Note: For firmware versions lower than 5.00 there is one common deadband used both for angles and magnitudes in the in
the corresponding phasor measurement (current or voltage). So take into account this when using reports with data
change, because in some cases the angle value can trigger reports quite often due to the difficulty to calculate a common
deadband for both values, angle and magnitude. In these cases it is advisable to use integrity report in firmware versions
lower than 5.00.
Starting from firmware version 5.00 the 650 family of relays implement separate deadbands for magnitude and angle for
phasors (voltages and currents). Thus for example, phase A current attribute contains in 650 relay two deadbands, one for
phase A current magnitude and the other for phase A current angle. The deadband for magnitude is the db parameter
while the deadband for angle is the dbAng parameter.
Apart from MMXU logical node also MSQI and Remote Input GGIO (default name rinGGIO1) have attributes that are
analogue values and contain db parameters to establish deadbands.
For firmware version below 7.00, deadbands shall be available in ICD/CID tab.
CONFIGURATION OF CONTROLLABLE OBJECTS
In the F650 relay IEC 61850 controllable data exist in logical nodes vinGGIO, XCBR and CSWI. Data from Logical node
vinGGIO maps to Virtual Inputs of F650. XCBR represents the circuit breaker and all four CSWI logical nodes represent four
first switchgear of F650 relay.
Controllable data in vinGGIO logical node are SPCSO1 - SPCSO64 and DPCSO1 - DPCSO16. Signals SPCSO1 - SPCSO32 map
to 32 Virtual Inputs Latched in F650 relay and signals SPCSO33 - SPCSO64 map to Virtual Inputs Self-Reset. DPCSO1 -
DPCSO16 are double control points and operate on pairs of Virtual Inputs Latched. Thus DPCSO1 - DPCSO16 map to 32
Virtual Inputs Latched and an operation of one attribute DPCSO always operate on two Virtual Inputs Latched, one Virtual
Input of the pair is set to "1" and the other Virtual Input of the pair is set to "0".
Controllable data in XCBR and CSWI logical nodes are Pos (position) objects. These are operations used to change state of
breaker or switch.
F650 relay supports all four IEC 61850 control modes (ctlModel), which are:
Direct control with normal security
SBO control with normal security
Direct control with enhanced security
SBO control with enhanced security
However for data in vinGGIO logical node only "direct control with normal security" mode of control can be used.