CHAPTER 7: IEC 61850 PROTOCOL 7.3 IEC 61850 CONFIGURATOR
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 7-245
Mapping of signals to rouGGIO1 indications is performed in Enervista 650 Setup software in menu Setpoint > Relay
Configuration > Remote Outputs. rouGGIO1 indications are called Rem GOOSE Dig Out 1, Rem GOOSE Dig Out 2, etc. in
this menu, and are listed after the DNA and UserSt bits.
By default the F650 contains one Data Set for configurable transmission GOOSE. This Data Set if formed by 8 elements,
these elements are 4 first rouGGIO1 indications and its associated quality flags. However no mapping is done by default to
rouGGIO1 indication in "Relay Configuration" (it must be done by the user with the desired signals)
Figure 7-34: Example of rouGGIO mapping in relay configuration
If the user tries to enable Fixed GOOSE but there are already 4 configurable transmisison GOOSEs already defined the
following error is shown:
If Fixed GOOSE is enabled a maximum of 3 configurable transmission GOOSEs can be defined. When trying to define more
configurable transmission GOOSEs the following error is shown: