APPENDIX B: MODBUS PROTOCOL B.5 MEMORY MAP
GEK-106310-AF F650 DIGITAL BAY CONTROLLER B-79
0x24D8 Confirmation address W 1
Ajustes Sobreintensidad Temporizada de Tierra Sensible Grupo 3 - Sensitive Ground TOC 3 Settings
0x24D9 Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x24DA Input F012 1 R/W 1 0=PHASOR(DFT)
1=RMS
0x24DB Pickup Level F003 1 R/W 2 [0.005 , 16.000] A
0x24DD Curve F012 1 R/W 1 0=IEEE Ext Inv
1=IEEE Very Inv
2=IEEE Mod Inv
3=IEC Curve A
4=IEC Curve B
5=IEC Curve C
6=IEC Long-Time Inv
7=IEC Short-Time Inv
8=IAC Ext Inv
9=IAC Very Inv
10=IAC Mod Inv
11=ANSI Ext Inv
12=ANSI Very Inv
13=ANSI Norm Inv
14=ANSI Mod Inv
15=I2t
16=Definite Time
17=Rectifier Curve
18=User Curve A
19=User Curve B
20=User Curve C
21=User Curve D
0x24DE TD Multiplier F003 1 R/W 2 [0.00 , 900.00] s
0x24E0 Reset F012 1 R/W 1 0=INSTANTANEOUS
1=LINEAR
0x24E1 Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x24F4 Confirmation address W 1
Ajustes Subtensión de Fases Grupo 1 - Phase UV 1 Settings
0x24F5 Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x24F6 Mode F012 1 R/W 1
0=PHASE-PHASE
1=PHASE-GROUND
0x24F7 Pickup Level F003 1 R/W 2 [3 , 300] V
0x24F9 Curve F012 1 R/W 1 0=DEFINITE TIME
1=INVERSE TIME
0x24FA Delay F003 1 R/W 2 [0.00 , 900.00] s
0x24FC Minimum Voltage F003 1 R/W 2 [0 , 300] V
0x24FE Logic F012 1 R/W 1 0=ANY PHASE
1=TWO PHASES
2=ALL PHASES
0x24FF Supervised by 52 F012 1 R/W 1 0=DISABLED
1=ENABLED
ADDRESS BIT NAME FORMAT STEP MODE LENGTH MISCELLANEOUS