B-142 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
B.5 MEMORY MAP APPENDIX B: MODBUS PROTOCOL
1=ENABLED
0x41B0 Min. Voltage F003 1,000 R/W 2 [0.00 , 300.00] V
0x41B2 Reach F003 1,000 R/W 2 [0.02 , 250.00] Ohm
0x41B4 Angle F003 1,000 R/W 2 [5 , 50] Deg
0x41B6 Pickup Delay F003 1,000 R/W 2 [0.000 , 65.535] s
0x41B8 Reset Delay F003 1,000 R/W 2 [0.000 , 65.535] s
0x41BA Snapshot Events F012 1,000 R/W 1 0=DISABLED
1=ENABLED
0x41CD Confirmation address W 1
Inversión de carga 3-Load Encroachment 3
0x41CE Function F012 1,000 R/W 1 0=DISABLED
1=ENABLED
0x41CF Min. Voltage F003 1,000 R/W 2 [0.00 , 300.00] V
0x41D1 Reach F003 1,000 R/W 2 [0.02 , 250.00] Ohm
0x41D3 Angle F003 1,000 R/W 2 [5 , 50] Deg
0x41D5 Pickup Delay F003 1,000 R/W 2 [0.000 , 65.535] s
0x41D7 Reset Delay F003 1,000 R/W 2 [0.000 , 65.535] s
0x41D9 Snapshot Events F012 1,000 R/W 1 0=DISABLED
1=ENABLED
0x41EC Confirmation address W 1
Max. Number of Starts
0x41ED Function F012 1000 R/W 1 0=DISABLED
1=ENABLED
0x41EE Full Load Amps F003 1000 R/W 2 [0,5 , 10,0] A
0x41F0 Breaker Supervision F012 1000 R/W 1 0=DISABLED
1=ENABLED
0x41F1 Min. Stop Time F003 1000 R/W 2 [0,0 , 900,0] s
0x41F3 Number of starts F004 1000 R/W 1 [0 , 10]
0x41F4 Time to restart F004 1000 R/W 1 [0 , 100] min
0x41F5 Reset counter F012 1000 R/W 1 0=DISABLED
1=ENABLED
0x41F6 Snapshot Events F012 1000 R/W 1 0=DISABLED
1=ENABLED
0x4209 Confirmation address W 1
Ajustes Protocolo PROCOME - PROCOME Protocol Communication Settings
0x420A COMM Port F012 1 R/W 1 0=NONE
1=COM 1
0x420B Slave Number F004 1 R/W 1 [0 , 254]
0x4210 Confirmation address W 1
32N1 High - wattmetric Ground Fault High Level Group 1 Settings
0x44A0 Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x44A1 Voltage Pickup Level F003 1 R/W 2 [2.00 , 70.00] V
0x44A3 Current Selection F012 1 R/W 1 0=IN
1=IG
0x44A4 OC Pickup Level F003 1 R/W 2
[0.005 , 0.400] A
ADDRESS BIT NAME FORMAT STEP MODE LENGTH MISCELLANEOUS