APPENDIX C: DNP 3.0 PROTOCOL FOR F650 C.8 ANALOG INPUTS
GEK-106310-AF F650 DIGITAL BAY CONTROLLER c-23
The "Fault Type" is represented by enumeration value. The table below shows values with DNP3 setting "Other Scale Factor
= 1".
If the DNP3 setting "Other Scale Factor" has a value different from "1" then "Enum Value" is scaled by the adjusted factor.
For example if "Other Scale Factor = 0.001", then the value corresponding to "TRIPH" fault type is 2000.
NAF indicates that the type of fault has not been calculated.
112 Board J - Analog 1
113 Board J - Analog 2
114 Board J - Analog 3
115 Board J - Analog 4
116 Board J - Analog 5
117 Board J - Analog 6
118 Board J - Analog 7
119 Board J - Analog 8
ENUM VALUE FAULT TYPE
0 GROUND
1 PHASE
2 TRIPH
3 AG
4 ABG
5 AB
6 BG
7 BCG
8 BC
9 CG
10 CAG
11 CA
12 NAF
POINT DESCRIPTION UNIT