7-74 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
2.2.2.5 gndPTOC
This logical node class is used for ground time overcurrent and sensitive ground time overcurrent. There are 6 instances
inside of this logical node inside the device. 3 for ground and 3 for sensitive ground time overcurrent.
2.2.2.6 gndPTOC_2
This logical node class is used for ground time overcurrent and sensitive ground time overcurrent when setting group
option is enable. There are 2 instances inside of this logical node inside the device, 1 for ground and 1 for sensitive ground
time overcurrent. This logical node class is available only for firmware version below 7.50
PTOC class
Attribute
Name
Attr.
Type
Explanation M/O notes
PTOC Time overcurrent
Data
Common Logical Node Information
Mod ModENC Mode M
Beh BehENS Behaviour M
Health HealthENS Health M
NamPlt LPL Name plate M
Status Information
Str PhsACD Start M TOC PKP
Op PhsACT Operate M TOC OP
Blk SPS Block O TOC BLK
Settings
PTOCEna SPG Function O
InMagTyp ING_0 Input O
StrVal FloatASG Pickup level O
TmACrv CURVE Curve O
TmMult geFloatASG TD Multiplier O
RsMod geING_0 Reset O
SnpshtEvEna geSPG Snapshot events enabled O
PTOC class
Attribute
Name
Attr.
Type
Explanation M/O notes
PTOC Time overcurrent
Data
Common Logical Node Information
Mod ModENC Mode M
Beh BehENS Behaviour M
Health HealthENS Health M
NamPlt LPL Name plate M
Status Information
Str PhsACD Start M TOC PKP
Op PhsACT Operate M TOC OP
Blk SPS Block O TOC BLK
Settings
PTOCEna SPG_2 Function O
InMagTyp ING_0_2 Input O
StrVal FloatASG_2 Pickup level O
TmACrv CURVE_3 Curve O
TmMult FloatASG_2 TD Multiplier O
RsMod ING_0_2 Reset O
SnpshtEvEna SPG_2 Snapshot events enabled O