7-104 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.2 IEC 61850 PROFILE FOR F650 CHAPTER 7: IEC 61850 PROTOCOL
In the F650 there are up to 16 configurable switchgears. Currently sixteen XSWI and sixteen CSWI are implemented and
mapped to all switchgears in F650. XSWI and CSWI Logical Nodes can be seen as paired objects in F650 as one pair of
XSWI and CSWI map to the same switchgear. XSWI1 and CSWI1 map to Switchgear1, XSWI2 and CSWI2 map to
Switchgear2, etc. The difference between XSWI and CSWI in F650 is that control commands cannot be sent directly via
XSWI LN. Control commands have to be sent via CSWI LN.
In F650 relay the Circuit Breaker (XCBR1 Logical Node) by default is mapped to first switchgear (exactly like XSWI1 and
CSWI1 LNs). However it is possible to map the Circuit Breaker to any of the 16 switchgears of F650 relay. It can be done by
modification of the following setting: Setpoint > System Setup > Breaker Settings > Number of Switchgear.
In XCBR LN for "Pos" controllable attribute all possible control models are applicable:
"direct-control-with-normal-security"
"SBO-control-with-normal-security"
"direct-control-with-enhanced-security"
"SBO-control-with-enhanced-security"
The sboTimeout attribute for Pos is configurable in a range from 500 ms to 60 seconds.
The sboClass attribute for Pos can only have value "0" (operate-once).
2.7.2 XSWI (Circuit switch)
In the F650 there are up to 16 configurable switchgears. Currently sixteen XSWI and sixteen CSWI are implemented and
mapped to all switchgears in F650. XSWI and CSWI Logical Nodes can be seen as paired objects in F650 as one pair of
XSWI and CSWI map to the same switchgear. XSWI1 and CSWI1 map to Switchgear1, XSWI2 and CSWI2 map to
Switchgear2, etc. The difference between XSWI and CSWI in F650 is that control commands cannot be sent directly via
XSWI LN. Control commands have to be sent via CSWI LN. "Pos" attribute is not controllable in XSWI it has ctlModel =
Status-only. In order to control the switch mapped to given XSWI the corresponding CSWI LN should be used.
XCBR class
Attribute
Name
Attr.
Type
Explanation M/O notes
XSWI Circuit switch
Data
Common Logical Node Information
Mod ModENC Mode M
Beh BehENS Behaviour M
Health HealthENS Health M
NamPlt LPL Name plate M
Status information
Loc SPS Local operation M Local / Remote
EEHealth EEHealthENS Ext. equipment health O
OpCnt INS Operation counter M Breaker openings
Controls
Pos DPC_2 Switch position M Breaker open, close
BlkOpn SPC_1 Block opening M Virtual output
BlkClr SPC_1 Block closing M Virtual output
SwTyp SwTypENS Switch type M
SwOpCap SwOpCapENS Switch operating capability

Table of Contents