CHAPTER 7: IEC 61850 PROTOCOL 7.2 IEC 61850 PROFILE FOR F650
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 7-139
2.2.11 PTRC (Protection trip conditioning)
2.2.11.1 PTRC
This logical node shall be used to connect the operate outputs of one or more
protection functions to a common trip to be transmitted to XCBR logical node and has 1 instance inside the device.
2.3 Logical Nodes for protection related functions. LN Group: R
2.3.1 RDIR (Directional element)
2.3.1.1 gePhsRDIR_2
This logical node class is used for phase directional elements and has 3 instances inside the device.
ConsTmCool geFloatASG_1_2 Cool time constant E
StrVal geFloatASG_2 Pickup level O
AlmVal geFloatASG_2 Alarm level O
EventEna geSPG_2 Snapshot events enabled E
PTRC class
Attribute
Name
Attr.
Type
Explanation M/O notes
PTRC Trip bus
Data
Common Logical Node Information
Mod geModINC Mode M
Beh geBehINS Behaviour M
Health geHealthINS Health M
NamPlt geLPL Name plate M
Status Information
Op geGeneralACT Operate M
RDIR class
Attribute
Name
Attr.
Type
Explanation M/O notes
RDIR Directional Element
Data
Common Logical Node Information
Mod geModINC Mode M
Beh geBehINS Behaviour M
Health geHealthINS Health M
NamPlt geLPL Name plate M
Status Information
Dir gePhsACD Direction M
Op gePhsACT Operate O
Blk geSPS_1 Block O
BlkIn geGeneralACT_1 Block Input O
Settings
RDIREna geSPG_2 Function O
ChrAng geFloatASG_2 Characteristic angle O
PolOpMod geING_0_2 Direction O
BlkMod geING_0_2 Block Logic O
BlkValV geIntASG_3 Minimum operating current O
VMemTms geFloatASG_1_2 Voltage Memory Time O
EventEna geSPG_2 Snapshot events enabled O