CHAPTER 7: IEC 61850 PROTOCOL 7.3 IEC 61850 CONFIGURATOR
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 7-221
Use DOI & DAI" setting:
"If this setting is set to False: the relay works only with the settings located in the relay's e2prom and the changes
performed on the ICD settings for the protection and control functions are only stored on the ICD file but not updated
in the relay.
"If this setting is set to true, the user is selecting the ICD
file settings to prevail over the relay settings. This means that
after changing settings in the ICD and powering the relay off and on the unit works with the settings included in the
ICD.
All setting changes performed through the HMI or EnerVista 650 Setup are automatically updated over the ICD file, likewise
if there is any change in the ICD file these changes are updated in the relay settings. The relay starts working with the new
ICD file after sending the file to the unit and powering the relay off and on.
The use of DOI & DAI has an enumerated value to determine its internal status, it is located in Actual Values > Status >
System info. Two different status shall reported: ICD STATUS AND ICD STATUS NOT VAL
Definitions of different values, which can be reported in both statuses, are described in tables below:
ICD STATUS
UNKNOWN: When the relay has not the IEC61850 protocol in the
relay model the ICD status is unknow to the unit.
ICD ERROR: There is an error in the ICD file and the relay ICD is not
operative. To solve this issue it is necessary to send a correct ICD to
the relay using the
IEC61850 configurator tool. When the ICD error is raised the IEC
61850 is not operative (the IEC 61850 client, reports and gooses do
not work). It is advisable to include the ICD ERROR in the main error
signal configured for specific applications.
MODIFIED: The settings have been changed in the icd but they are
still not written in the icd file in the relay
IN PROGRESS: The icd setting are being written to the file in the
relay.
OK WITHOUT DAIS: The relay has not got the "Use DOI &DAI" setting
enabled
(true) and it is working properly with the ICD file.
OK: The relay has got the "Use DOI &DAI" setting enabled (true) and
it is working properly with the ICD file. When that setting is set to
true the icd setting prevails over the relay settings
DEAFULT: There is no CID file in notvalidated neither in validated
and default CID has been loaded. After a reboot, default CID file is
considered as a normal CID file.
ERROR HEADER CID: there is a discrepancy in the information about
product model or firmware version between the firmware of the
relay and the CID file. If this message is displayed, relay shall not be
able to communicate by using IEC 61850 until this discrepancy is
solved. CID version and firmware version must match in order to get
complete functional relay.
ERROR SG CID is displayed if the relay has the Setting Group
function disabled but the managed CID file has the Settings Groups
available or the relay has the Setting Group function enabled but
the managed CID file has the Settings Groups not available.