7-222 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
7.3 IEC 61850 CONFIGURATOR CHAPTER 7: IEC 61850 PROTOCOL
1. Take into account that if the ICD status is "MODIFIED" or "IN PROGRESS" it is not advisable to switch off the unit
because the latest settings would not be stored in the unit.
2. In case that ERROR SG CID is displayed in ICD Status, ens
ure managed CID has Setting Group enable if Setting Groups
function is enable or ensure managed CID has Setting Group disable if Setting Groups function is disable.In order to
allow user to work with correct CID, two default files shall be created in IEC61850 folder when Enervista 650 PC is
installed.
• "default_F650SG_v7XX.cid: CID file with
setting group option enable
• "default_F650_v7XX.cid: CID file with setting gr
oup option disable.
Figure 7-18: default CID files
3. Take into in account that if ERROR HEADER CID value is being displayed in ICD STATUS or ICD STATUS NOT VAL section
in Act
ual Values > Status > System info, relay shall not be able to communicate by using IEC 61850 until this
discrepancy is solved. CID version and firmware version must match in order to get complete functional relay.
Use Setting Group" setting:
The attribute called "Use Setting Group" has been implemented for the IED in the ICD file in order to set if the SGCB is going
to be available in the relay or not.
This attribute is not available for firmware versions 7.20 or above. The user shall use proper CID file depending if Setting
Group function is enabled or disabled.
ICD STATUS NOTVAL UNKNOWN: No 61850 protocol
ERROR: The CID file in notvalidated is not valid
NOTVALIDATED EMPTY: There is no CID file in notvalidated
PASSED TO VALIDATED: New valid CID file in notvalidated y and
passed to validated
ERROR HEADER CID: There is a discrepancy in the information about
product model or firmware version between the firmware of the
relay and the CID file. If this message is displayed, relay shall not be
able to communicate by using IEC 61850 until this discrepancy is
solved. CID version and firmware version must match in order to get
complete functional relay.
I