CHAPTER 7: IEC 61850 PROTOCOL 7.3 IEC 61850 CONFIGURATOR
GEK-106310-AF F650 DIGITAL BAY CONTROLLER 7-229
Firmware versions from 7.20 to below 7.50
Firmware versions 7.50 and above
Figure 7-24: IEC 61850 Configurator
The setting grouping permission can be enabled or disabled using the relay HMI or using menu path Setpoint > Control
Elements > Setting Group in the EnerVista 650 Setup program as shown in the figure.
For versions below 7.50 it can be enabled or disabled in the IEC61850 Configurator by setting Use Setting Group to true or
false.