B-118 F650 DIGITAL BAY CONTROLLER GEK-106310-AF
B.5 MEMORY MAP APPENDIX B: MODBUS PROTOCOL
16=Definite Time
17=Rectifier Curve
18=User Curve A
19=User Curve B
20=User Curve C
21=User Curve D
0x32E4 TD Multiplier F003 1 R/W 2 [0.00 , 900.00] s
0x32E6 Reset F012 1 R/W 1 0=INSTANTANEOUS
1=LINEAR
0x32E7 Voltage Restraint F012 1 R/W 1
0=DISABLED
Ajustes Sobreintensidad Temporizada de Fases Nivel Alto Grupo 3 - Phase TOC Low 3 Settings(cont.)
1=ENABLED
0x32E8 Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x32FB Confirmation address W 1
Ajustes Aparamenta (16 elementos) - Switchgear Settings (16 items)
0x32FC CONTACTS TYPE_01 F012 1 R/W 1 0=52a + 52b
1=52a
2=52b
3=NONE
0x32FD CONTACTS TYPE_02 F012 1 R/W 1 0=52a + 52b
1=52a
2=52b
3=NONE
... ... ... ... ... ... ... ...
0x330B CONTACTS TYPE_16 F012 1 R/W 1 0=52a + 52b
1=52a
2=52b
3=NONE
0x330C FAIL TO OPEN 01 t F004 1 R/W 1 [0 , 30000] ms
0x330D FAIL TO OPEN 02 t F004 1 R/W 1 [0 , 30000] ms
... ... ... ... ... ... ... ...
0x331B FAIL TO OPEN 16 t F004 1 R/W 1 [0 , 30000] ms
0x331C FAIL TO CLOSE 01 t F004 1 R/W 1 [0 , 30000] ms
0x331D FAIL TO CLOSE 02 t F004 1 R/W 1 [0 , 30000] ms
... ... ... ... ... ... ... ...
0x332B FAIL TO CLOSE 16 t F004 1 R/W 1 [0 , 30000] ms
0x332C Snapshot Events SWGR 1 F012 1 R/W 1 0=DISABLED
1=ENABLED
0x332D Snapshot Events SWGR 2 F012 1 R/W 1 0=DISABLED
1=ENABLED
... ... ... ... ...
... ... ...
0x333B Snapshot Events SWGR 16 F012 1 R/W 1 0=DISABLED
1=ENABLED
0x334C Confirmation address W 1
Ajustes Interruptor - Breaker Settings
0x334D Number of Switchgear F004 1 R/W 1 [1 , 16]
0x334E Maximum KI2t F003 1 R/W 2 [0.00 , 9999.99] (KA)2 s
0x3350 KI2t Integ. Time F003 1 R/W 2 [0.03 , 0.25] s
0x3352 Maximum Openings F004 1 R/W 1
[0 , 9999]
ADDRESS BIT NAME FORMAT STEP MODE LENGTH MISCELLANEOUS