APPENDIX F: IEC 60870-5-103 PROTOCOL F.1 IEC 60870-5-103 PROTOCOL
GEK-106310-AF F650 DIGITAL BAY CONTROLLER f-3
Earth fault indications in monitor direction
Fault indications in monitor direction
<35> Phase sequence supervision
X
<36> Trip circuit supervision 4539 BREAKER FAIL
SUPERVISION
<37> I>> back-up operation
X <38> VT fuse failure 4545 VT FUSE FAILURE
<39> Teleprotection disturbed
<46> Group warning
<47> Group alarm
INF Semantics F650 Identifier F650 Data Text
<48> Earth fault L1
<49> Earth fault L2
<50> Earth fault L3
<51> Earth fault forward, i.e. line
<52> Earth fault reverse, i.e. busbar
INF Semantics F650 Identifier F650 Data Text
X
<64> Start / pick-up L1 3997|4013|4029|4045|4061|4077|41
64|4182|4200|565
1|5669|5687
PH IOC/TOC 1/2/3
H/L A PKP
X
<65> Start / pick-up L2 3999|4015|4031|4047|4063|4079|41
66|4184|4202|565
3|5671|5689
PH IOC/TOC 1/2/3
H/L B PKP
X
<66> Start / pick-up L3 4001|4017|4033|4049|4065|4081|41
68|4186|4204|565
5|5673|5691
PH IOC/TOC 1/2/3
H/L C PKP
X
<67> Start / pick-up N 4112|4120|4128|4239|4248|4257 GROUND IOC/TOC
1/2/3 PKP
X
<68> General trip 4004|4020|4036|4052|4068|4084|41
71|4189|4207|565
8|5676|5694
PH IOC/TOC 1/2/3
H/L OP
X
<69> Trip L1 3998|4014|4030|4046|4062|4078|41
65|4183|4201|565
2|5670|5688
PH IOC/TOC 1/2/3
H/L A OP
X
<70> Trip L2 4000|4016|4032|4048|4064|4080|41
67|4185|4203|565
4|5672|5690
PH IOC/TOC 1/2/3
H/L B OP
X
<71> Trip L3 4002|4018|4034|4050|4066|4082|41
69|4187|4205|565
6|5674|5692
PH IOC/TOC 1/2/3
H/L C OP
<72> Trip I>> (back-up operation)
<73> Fault location X in ohms
<74> Fault forward / line
<75> Fault forward / lbusbar
<76> Teleprotection signal
tran
smitted

Table of Contents